How to resolve the discrepancy between the output current and displayed current on the GD350?
2026-01-29
A

The VFD outputs a Pulse Width Modulation (PWM) waveform, not a utility-frequency sinusoidal wave. It consists of a series of high-frequency voltage pulses (typically in the range of several kHz to tens of kHz), whose fundamental frequency is the motor operating frequency you set (e.g., 50Hz). Ordinary AC clamp meters (especially non-"True RMS" types) are designed and calibrated to measure pure 50/60Hz sine waves. They cannot accurately measure the true RMS value of non-sinusoidal waves like PWM, which are rich in harmonics, and this typically results in significantly lower readings.

You can use the same clamp meter to measure the current on the input side (R/S/T terminals) of the VFD. If the clamp meter reading for the input current is also much lower than the output current displayed by the VFD (for example, only around 7-8A on the input side), this provides strong evidence that your clamp meter is not suitable for measuring the VFD output. Only if the input side current reading is close to the output side displayed value (11.9A) should you suspect an issue with the VFD's internal detection circuit.

For on-site measurement verification, be sure to purchase or borrow a "True RMS" clamp meter

Q
Why does the GD350A keypad current differ from the clamp meter reading?
2026-01-29
A

The VFD outputs a pulse width modulation (PWM) waveform rather than a utility frequency sine wave. It consists of a series of high-frequency voltage pulses (typically ranging from several kHz to tens of kHz), with its fundamental frequency being the motor operating frequency you set (e.g., 50 Hz). Standard AC clamp meters (especially non-RMS types) are designed and calibrated to measure pure 50/60Hz sine waves. They cannot accurately measure the true RMS value of non-sinusoidal waves like PWM (which are rich in harmonics), often resulting in significantly low readings. For field verification measurements, always use an RMS clamp meter.

Q
How can I resolve the issue of running the GD350 directly from a specific frequency?
2026-01-23
A

To enable the inverter to start directly from a specific frequency, configure the settings as follows:
Start-up Mode Configuration:
· Select the ‘Direct Start’ mode in function code P01.01 (set to 0)
· Set function code P01.02 (Direct Start Start Frequency) to the desired specific frequency
Frequency Command Configuration:
· Select the frequency command source via function code P00.06, configurable as Function Code Setting (0) or Analogue Setting (1-4)
· If Function Code Setting is selected, set the operating frequency to the specific value via P00.13
Control Mode Verification:
· Ensure the operating command channel (P00.01) is set to the correct control mode (e.g., Local Control, Communication Control)
· Upon receiving the run command, the drive will start directly from the specified frequency
This start method is suitable for applications requiring rapid attainment of a specific rotational speed. The drive will commence output directly from the set frequency without accelerating from 0Hz.

Q
How to resolve the issue where the GD5000 fails to become ready after high voltage power-up and displays “POFF”?
2026-01-23
A

1. Check the fault history and current alarms. Review the historical fault records on the HMI, as they may reveal the root cause of the POFF condition.

2. Verify control and auxiliary power supplies. Ensure all low-voltage circuit breakers and switches in the control cabinet are closed. If a UPS is present, check its operational status. Alternatively, open the VFD control cabinet door and observe whether indicator lights for all power modules (e.g., PLC power supply, trigger power supply, drive board power supply) are lit normally (typically green indicates normal operation).

3. Verify all interlock and safety signals. An unclosed safety interlock circuit will force the system into POFF. Check external safety interlock signals on user terminals—including emergency stop, remote/local switch, fan fault, and transformer overtemperature signals—to ensure they are in normal state (typically normally open or normally closed contacts). Simultaneously confirm all cabinet doors (switchgear, transformer, control) are fully closed.

Q
Why does the frequency jump from 0 to a certain value when starting the inverter without connecting the motor?
2026-01-23
A

This frequency jump from 0 to a specific value is typically a parameter setting issue rather than a fault. Reset the parameters and restart to see if it resolves. Typically, parameter P01.01 sets the initial frequency during inverter startup, causing the inverter to start at the frequency specified in P01.01. Alternatively, parameters P08.08 and P08.09 may be configured to bypass undesired frequency levels and jump directly to the target frequency. These parameters can all cause the inverter frequency to jump abruptly.

Q
What causes an UL under-voltage fault on GD350 after the motor is connected?
2026-01-23
A

If it operates normally without the motor, an under-voltage fault with the motor connected usually indicates the relay is not functioning. Power on and listen for the relay clicking into place. The relay operates on internal 24V power. If no sound is heard, disconnect the fan power cable at the top, then power on again and check for the relay clicking sound. If still absent, this indicates no internal 24V power. Replace the relay or the internal power board.

Q
How to resolve the connection failure issue when setting a high baud rate on DA200 P4.03?
2026-01-23
A

When configuring parameter P4.03, if you find that a low baud rate connects successfully but 56700 fails, this may indicate a switching frequency issue. Check P9.53. If its current value is 4k, change it to 8k before attempting connection again (P9.53 requires developer permissions; contact INVT engineers in advance if needed).

Q
How to switch from PV control or three-phase input to single-phase utility input for single-phase output?
2026-01-23
A

Q: How do I configure parameters to switch from PV control or three-phase utility power to single-phase utility power for single-phase output?
A: First, set parameter P15.00 to 0 to disable the PV function, ensuring the SP100 is powered by mains frequency. Set P15.39 to 0 to change the product model to single-phase power supply with single-direction output (this function code can also be used to switch the product model to match different input/output configurations). After verifying the wiring is correct, power on and start the system.

Q
What is the function of the TF card in the GD880 and what are the precautions for replacing it?
2026-01-23
A

The TF card stores control parameters, system operation data and black box data. It is located on the left side of the control unit and can be used to restore parameters for a new control unit.

The TF card can be replaced after the main control unit is powered off. To avoid damaging the TF card, it should be removed before the control unit protective cover is removed.