The inverter motor of the friction welding machine adopts the INVT inverter motor, and the incremental type 2500 line parameters adopted by the encoder are as follows:


Equipment selection:

No.NameVoltageSpeedMotor PowerCurrentTorque
1Motor380V1500rpm30KW59A195NM

Model and parameters of INVT frequency converter:

No.NameVoltageModelCurrentQuantity
1Frequency Inverter380vGD350-037G-475A1 piece
2

10Ω, 15KW
1 piece


Control sequence:

1. PLC gives the starting signal. The servo motor drives the rotary jig to rotate at high speed.

2. When the rotating fixture rotates at a high speed, the hydraulic system pushes the sliding table forward and gradually begins to weld. Meanwhile, the pushing pressure of the sliding table increases gradually.

3. when the welding is completed, PLC gives the spindle back to zero models, rotating fixture fast and accurate positioning to zero, at the same time, the top forging pressure plus a high pressure to ensure that the welding is firm.

4. After the frequency converter outputs the positioning signal and maintains the voltage for a period of time, the sliding table will automatically return and start the next welding, and so on.


Debug instructions

The frequency converter adopts speed control at the beginning of welding and pulse position control at positioning. In order to ensure accurate positioning, relevant parameters of position ring and speed ring must be adjusted to appropriate values.

1. Check the wiring according to the electrical schematic diagram.

2. Input motor parameters for self-learning.

3. The speed response and positioning accuracy effect shall be measured at no load to properly adjust the gain and acceleration and deceleration time of the speed ring and position ring.

4. After the no-load test, carry out the on-load test and fine-tune the parameters according to the actual effect.

5. Main parameters of frequency converter debugging:

P0.003
P0.03100
P0.04100
P0.110.4
P0.120.5
P0.145
P1.010.1
P1.150.1
P1.240.2
P3.0310
P3.092000
P3.102000
P3.20220
P3.21220
P3.35256
P05.011
P05.0245
P05.0363
P06.0330
P06.045
P8.38650
P11.030